I would like to learn more about large-scale UPS systems, particularly the battery strings used in traditional RBOC/Telco applications. These are the sort of beasts that use huge strings of 6V 220aH deep cycle batteries, or even large numbers of 2V 400aH batteries on very strong earthquake-resistant shelving wired up to create a 48V mega-battery. Can anyone point me to the most definitive reference materials on the subject?
One thing of note would be that phone equipment uses a -48v power source. SO the UPS system doesn't need to reconvert the battery power in order to power the equipment.
posted by gjc at 7:37 AM on December 17, 2009
posted by gjc at 7:37 AM on December 17, 2009
Liebert also makes some serious UPS systems.
Both APC and Liebert also publish white papers on a variety of telco and data center topics. They're available on their sites and may be another good source of information regarding design principles.
posted by Hoenikker at 7:41 AM on December 17, 2009
Both APC and Liebert also publish white papers on a variety of telco and data center topics. They're available on their sites and may be another good source of information regarding design principles.
posted by Hoenikker at 7:41 AM on December 17, 2009
In telco applications, much of this is either down to particular switching equipment manufacturers (e.g. Siemens, Alcatel, etc) or specialist - and often country-dependent - power system suppliers (e.g. a few Australian names come to mind). And the rest of the specs / info / design docs / etc will be locked up in internal telco engineering documents.
There's 2 basic types of power setups used by telcos - a centralised power room filled with enough rectifiers & batteries to power the whole exchange [CO in US-parlance], or distributed power systems consisting of smaller rectifiers and battery banks designed to power a few racks or a suite of equipment and distributed as-needed around the equipment floor. From the sound of your Q, you're interested in the former, though the latter is becoming more common.
FWIW, a few years ago when I was directly involved in maintaining this stuff, a 220Ah or 400Ah battery string was considered a small one. 3 or 4 banks (each 24 x 2.20V cells) of 220Ah batteries were used in small (500~1500 line) rural exchanges. Most suburban exchanges of a few thousand => 10-15,000 lines used multiple (3-6) 550Ah batteries. The biggest I ever dealt with myself used multiple banks of 2170Ah batteries in an exchange which drew upwards of 3000A @ 50V.
So the real question is "what do you want to know, exactly?". 'Cos the answer will differ greatly depending on style, size, type, etc.
posted by Pinback at 2:57 PM on December 17, 2009
There's 2 basic types of power setups used by telcos - a centralised power room filled with enough rectifiers & batteries to power the whole exchange [CO in US-parlance], or distributed power systems consisting of smaller rectifiers and battery banks designed to power a few racks or a suite of equipment and distributed as-needed around the equipment floor. From the sound of your Q, you're interested in the former, though the latter is becoming more common.
FWIW, a few years ago when I was directly involved in maintaining this stuff, a 220Ah or 400Ah battery string was considered a small one. 3 or 4 banks (each 24 x 2.20V cells) of 220Ah batteries were used in small (500~1500 line) rural exchanges. Most suburban exchanges of a few thousand => 10-15,000 lines used multiple (3-6) 550Ah batteries. The biggest I ever dealt with myself used multiple banks of 2170Ah batteries in an exchange which drew upwards of 3000A @ 50V.
So the real question is "what do you want to know, exactly?". 'Cos the answer will differ greatly depending on style, size, type, etc.
posted by Pinback at 2:57 PM on December 17, 2009
This thread is closed to new comments.
posted by gregr at 6:14 AM on December 17, 2009