"Subject: A word on voltages: 110/115/117/120/125/220/240Out on the pole that feeds your building are either 3 wires or 4 wires, depending on whether your distribution system delivers a neutral (many don't). A 4 wire system is often called a "Y" or "Wye" system, because that's how it's usually diagrammed [in this case, upside down], whereas a 3 Wire system is a "Delta" because the diagram for that kind of connection looks like the Greek letter delta. The "neutral" wire, if there is one in your distribution system, doesn't carry any current if the power being delivered by the 3 power phases is balanced, but if they are unbalanced, phantom voltage and current (reactive power components) will appear in the neutral leg. These "phantom" components are created by the service transformer at your location as it tries to balance the load you are creating. A Delta system doesn't try to balance the load, and will just have high (hot) or low phases if your loads are unbalanced. In both Y (Wye) and Delta systems, a ground leg is usually required, which should never carry current in normal operation, but provides an emergency path to ground stakes driven into the earth at the service entrance, should an insulation fault or other problem develop in a piece of electrical equipment. Many systems that deliver just the 3 phase legs to the pole transformer in a Delta distribution system will be connected on the secondary side for 4 wire Y distribution by electrically bonding the secondary neutral wires to grounding stakes driven into the earth near the service entrance, from wires taken out of the service transformer secondary winding, through the main disconnect switch. But a ground and neutral are not the same thing, and serve different purposes, although in normal conditions, neither may be carrying current, and both may be at the same electrical potential as the earth.
One thing where things might get a bit confusing is the
different numbers people bandy about for the voltage of
a circuit. One person might talk about 110V, another 117V
or another 120V. These are all, in fact, exactly the same
thing... In North America the utility companies are required
to supply a split-phase 240 volt (+-5%) feed to your house.
This works out as two 120V +- 5% legs. Additionally, since there
are resistive voltage drops in the house wiring, it's not
unreasonable to find 120V has dropped to 110V or 240V has dropped
to 220V by the time the power reaches a wall outlet. Especially
at the end of an extension cord or long circuit run. For a number
of reasons, some historical, some simple personal orneryness,
different people choose to call them by slightly different numbers.
This FAQ has chosen to be consistent with calling them "110V" and
"220V", except when actually saying what the measured voltage will
be. Confusing? A bit. Just ignore it.
One thing that might make this a little more understandable
is that the nameplates on equipment often show the lower (ie: 110V
instead of 120V) value. What this implies is that the device
is designed to operate properly when the voltage drops that
low.
208V is *not* the same as 240V. 208V is the voltage between
phases of a 3-phase "Y" circuit that is 120V from neutral to any
hot. 480V is the voltage between phases of a 3-phase "Y"
circuit that's 277V from hot to neutral.
In keeping with 110V versus 120V strangeness, motors intended
to run on 480V three phase are often labeled as 440V..."
How many horsepower to the motors on the machines draw? Are they 3-phase also? You can caculate the current draw with these two number, Ill dig up a chart for you.