SubscribeWhat's the purpose of the ground prong on an outlet, then?If you don't understand the bolded section (or anything else, really) I'm sure we can clarify further.
Apart from their use in electronics, which we won't comment on, and for certain fluorescent lights (they won't turn on without a good ground connection), they're intended to guard against insulation failures within the device. Generally, the case of the appliance is connected to the ground lead. If there's an insulation failure that shorts the hot lead to the case, the ground lead conducts the electricity away safely (and possibly trips the circuit breaker in the process). If the case is not grounded and such a short occurs, the case is live -- and if you touch it while you're grounded, you'll get zapped. Of course, if the circuit is GFCI-protected, it will be a very tiny zap -- which is why you can use GFCIs to replace ungrounded outlets (both NEC and CEC).
There are some appliances that should *never* be grounded. In particular, that applies to toasters and anything else with exposed conductors. Consider: if you touch the heating electrode in a toaster, and you're not grounded, nothing will happen. If you're slightly grounded, you'll get a small shock; the resistance will be too high. But if the case were grounded, and you were holding it, you'd be the perfect path to ground... [emphasis added]
Surges, spikes, zaps, grounding and your electronicsPersonally, I don't think surge suppression is particularly critical. It will depend a lot on how the power is where you live.
Theoretically, the power coming into your house is a perfect AC sine wave. It is usually quite close. But occasionally, it won't be. Lightning strikes and other events will affect the power. These usually fall into two general categories: very high voltage spikes (often into 1000s of volts, but usually only a few microseconds in length) or surges (longer duration, but usually much lower voltage).
Most of your electrical equipment, motors, transformer-operated electronics, lights, etc., won't even notice these one-shot events. However, certain types of solid-state electronics, particularly computers with switching power supplies and MOS semiconductors, can be damaged by these occurances. For example, a spike can "punch a hole" through an insulating layer in a MOS device (such as that several hundred dollar 386 CPU), thereby destroying it.
The traditional approach to protecting your electronics is to use "surge suppressors" or "line filters". These are usually devices that you plug in between the outlet and your electronics.
Roughly speaking, surge suppressors work by detecting overvoltages, and shorting them out. Think of them as voltage limiters. Line filters usually use frequency-dependent circuits (inductors, capacitors etc.) to "tune out" undesirable spikes - preventing them from reaching your electronics.
So, you should consider using suppressors or filters on your sensitive equipment.
These devices come in a very wide price range. From a couple of dollars to several hundred. We believe that you can protect your equipment from the vast majority of power problems by selecting devices in the $20-50 range.
A word about grounding: most suppressors and EFI filters require real grounds. Any that don't are next to useless.
For example, most surge suppressors use MOVs (metal oxide varistors) to "clamp" overvoltages. Yes, you can have a suppressor that only has a MOV between neutral and hot to combat differential-mode voltage excursions, but that isn't enough. You need common-mode protection too. Good suppressors should have 3 MOVs, one between each pair of wires. Which means you should have a good solid ground. Eg: a solidly connected 14ga wire back to the panel. Not rusty BX armour or galvanized pipe with condensation turning the copper connection green.
Without a ground, a surge or spike is free to "lift" your entire electronics system well away from ground. Which is ideal for blowing out interface electronics for printer ports etc. Secondly, static electricity is one of the major enemies of electronics. Having good frame grounds is one way of protecting against static zaps.
If you're in the situation of wanting to install computer equipment on two wire groundless circuits take note:
Adding a GFCI outlet to the circuit makes the circuit safe for you. But it doesn't make it safe for your equipment - you need a ground to make surge suppressors or line filters effective.
How do I convert two prong receptacles to three prong?I'm kind of torn about GFCI being equivalent to third prong ground - the protection is quite different - but who am I to argue..
Older homes frequently have two-prong receptacles instead of the more modern three. These receptacles have no safety ground, and the cabling usually has no ground wire. Neither the NEC or CEC permits installing new 2 prong receptacles anymore.
There are several different approaches to solving this:The CEC permits you to replace a two prong receptacle with a three prong if you fill the U ground with a non-conducting goop. Like caulking compound. This is not permitted in the NEC.
- If the wiring is done through conduit or BX, and the conduit is continuous back to the panel, you can connect the third prong of a new receptacle to the receptacle box. NEC mainly - CEC frowns on this practice.
- If there is a metallic cold water pipe going nearby, and it's electrically continuous to the main house ground point, you can run a conductor to it from the third prong. You MUST NOT assume that the pipe is continuous, unless you can visually check the entire length and/or test it. Testing grounds is tricky - see "Testing Grounds" section.
- Run a ground conductor back to the main panel.
- Easiest: install a GFCI receptacle. The ground lug should not be connected to anything, but the GFCI protection itself will serve instead. The GFCI will also protect downstream (possibly also two prong outlets). If you do this to protect downstream outlets, the grounds must not be connected together. Since it wouldn't be connected to a real ground, a wiring fault could energize the cases of 3 prong devices connected to other outlets. Be sure, though, that there aren't indirect ground plug connections, such as via the sheath on BX cable.
The NEC requires that three prong receptacles without ground that are protected by GFCI must be labelled as such.