Blowing some cool air on a hot server
March 15, 2012 6:08 AM Subscribe
Apparently as the air system in our office building has degraded, the heat in our offices during the spring and fall when the AC shuts off has become unbearable as air that is hotter than outside is blown around. Bad for people, but worse for our server room. It has gotten to the breaking point and we need to do something. I'm looking for a way to cool off our servers in the transition periods between winter and A/C being turned on.
The server room is about 10' x 20' and has a 16' ceiling. It isn't air tight and there is maybe a foot or two between the ceiling tiles and the next floor.
There are four servers, a PC, a Dell MD1000 storage device, and three APC 3000VA UPS. There is no exhaust out from the room and there is a fan that blows in air (hot air at the moment, probably not A/C for a few weeks at least.)
The building is in the middle of a messy change of ownership and we can't really do much to reconfigure the room itself, at least not any time soon.
My current thought is to purchase a portable AC unit and have it vent out over the ceiling of the next room (this is doable). However I'm not sure how good of an idea this is or how strong of an AC unit to get.
I'm sure there are all sorts of details I'm leaving out - I'll clarify as best I can. I inherited this setup and a lot of things are undocumented or unknown. Also, it is going to be 80 degrees today and the quicker fix the better!
posted by charred husk to computers & internet (13 answers total)
During the shoulder seasons, mechanical cooling might be locked out based on outdoor air temp or a schedule, but free cooling via economizer dampers should still be available. Your problem could be from a badly designed system, a failed economizer/mixed air damper actuator, or any number of other things.
As far as your actual question, about the portable AC unit, I have seen that on multiple occasions. Hell, my own office used a Costco portable AC unit to cool our server room until we got the tinbashers to get some ducting in there. Ours vented to the outdoors though, and I can't say how good an idea it is to vent the AC unit into a ceiling space. The ceiling space could well be feeding into the main system loop and thus you might be indirectly heating your supply air even more. Might be worth calling a local mechanical contractor to see what they have to say. The pain in the butt will be that you are dumping hot air in from the main system that you are then cooling with the portable AC unit.
posted by Sternmeyer at 6:31 AM on March 15, 2012