How many amps can my sub-panel hold?
March 6, 2012 11:47 AM Subscribe
Panel to Garage sub-panel. How many amps can my sub-panel hold? (You are not my electrician.)
I will be hiring a licensed electrician, I’m just curious as to what to expect.
The main house electrical service panel is connected to a sub panel in a detached garage.
The circuit on the main panel feeding the garage has a two pole breaker labeled 30 amps.
The garage sub panel has a one 20 amp circuit and one 15 amp circuit. There is room on the panel to add two more circuits.
My questions are:
It is my understanding that the circuit to the garage can be either a single 240 volt or two 120 volt. Is my understanding correct?
If this is correct, how many amps can I add to the garage sub-panel if it’s single 240?
Alternatively,
How many amps can I add to the garage sub-panel if it’s two 120?
Finally,
If this is completely wrong, let me know.
posted by otto42 to home & garden (3 answers total)
Not quite. The two-pole breaker in the main panel is connected to both 120V legs of the service coming into your house. Presumably the conductors from that breaker are in turn connected to the 2 sides of the sub-panel. Those 2 legs can be used to make either 120v or 240v circuits, depending on the type of breakers you install. A single-pole breaker in the sub-panel will connect to only one of those legs, and give you a 120v circuit. A double-pole breaker will connect to both legs and give you a 240v circuit. Make sense?
The breakers you put in the sub-panel shouldn't be any larger than the 30-amp breaker in the main panel that feeds it. I'm not sure what code and convention have to say about the relationship between that 30-amp breaker and the total amperage of all the breakers in the sub-panel, but from an electrical standpoint it doesn't necessarily matter. You could fill the sub-panel with 30-amp breakers and connect them all to 30-amp loads, and it would work as long as you only turned on one load at a time.
posted by jon1270 at 12:21 PM on March 6, 2012